    Warped steel lentil

    Facade inspection. Any thoughts on what is causing this steel lentil to warp? We have been inspecting buildings for 20 years and have never seen this before. It is all over the building, all sides including north facade so we have ruled out thermal expansion. It clearly wasn't built like that due to the gap that formed between the steel and the mortar. This is an apartment building built in the 1980s. Tried to upload the pic, I hope it worked. LOL
    Attached Images Attached Images

  2. #2
    Technical Fellow Kelly_Bramble's Avatar
    Join Date
    Feb 2011
    Location
    Bold Springs, GA
    Posts
    2,625
    Most likely it was warped on installation (welding or delivered that way) or compressive/bending loading due to foundation settling.
    Tell me and I forget. Teach me and I remember. Involve me and I learn.

  3. #3
    Associate Engineer
    Join Date
    Dec 2021
    Posts
    2
    Most of my replies on other boards are that it is water freezing and bending the lintel. No weep holes, Michigan.

  4. #4
    Technical Fellow Kelly_Bramble's Avatar
    Join Date
    Feb 2011
    Location
    Bold Springs, GA
    Posts
    2,625
    Frozen water? Sure, that's a possibility but how did the water get there in the volume needed to expand and warp the lintel?

    I think I see a reflection on the glass and an eves above.
    Tell me and I forget. Teach me and I remember. Involve me and I learn.